    I need to know, how many GPM does the oo7 pump rates ?
  • Empire_2
    Empire_2 Member Posts: 2,340
    Taco.com
    A nice web sight that has all the info you are looking for. Flow will depend on pipe size and length for rated head/GPM/BTU you wish to convey.
    Mike T.
  • Joe Mattiello
    Joe Mattiello Member Posts: 751
    007 operating characteristics
    Good Morning
    Your question is not unique, and not easily answered with a specific number. Every centrifugal pump has a flow/head curve and the net flow is dictated by the system resistance. If you look at the 007 performance curve you will see it can create approximately 12 feet of head at shut off, and will deliver approximately 22 gpm when pumping against little or no resistance. Where the 007 operates on its curve in your system is dictated by the system dynamics.
    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions
  • carol_3
    carol_3 Member Posts: 397
    Thanks for the good info, guys.
  • Empire_2
    No reply
    It would be so nice if the ask-er of the question would reply so that we know that his or her Q: were answered. It's kinda like letting someone out into traffic in front of you and they do not wave as a gesture of thank's.
    Mike T.
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Here in Boston, Carol
    we always wave.
    Some of the time we actually use all five fingers