BTU rating for cast iron radiators
Biker
Member Posts: 1
Looking for a chart that explains the BTU ratings for different size cast iron radiators.
Thanks
Rich
Thanks
Rich
Radiator Btu's
Go to "SHOP" on the overhead task bar and get Dan's book, "EDR..every darn radiator". Short of that you can find a professional in your area who has one, or post pics and dimensions of ALL your radiators and hope one of us has the kindness and patience to figure it for you.0 -
We also need to know
if you're working on a hot-water or steam system. BTU output differs dramatically between the two.
Especially if
you are modulating your hot water temperature.
As a general rule for CI radiators (measured in square feet EDR or "Equivalent Direct Radiation") emit BTU's per hour (BTUH) in a 70 degree room as follows:
215 degrees (steam basis rating) 240 BTUH per EDR
Hot Water at AVERAGE water temperatures (halfway between supply and return temperature at the radiator):
170 F = 150 BTUH
160 F = 130 BTUH
150 F = 110 BTUH
140 F = 90 BTUH
130 F = 70 BTUH
120 F = 50 BTUH
100 F = 30 BTUH
90 F = 10 BTUH
All in a 70 F room remember.0 -
So Kind
Brad, I'm gonna cut and paste those figures for myself. A god among men? Well...you're working on it.
TG0 -
You are too kind, Tom
Thanks for the kind words but I am far from there. Just trying to help where I can.
BEW0
- 116 Geothermal
- 15.8K Strictly Steam
