reversing flow direction on a series loop

Options
In principal it should work, but in theory, you should do proper heat loss for each room and determine the need vs. output at design temp. Go figure!

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=248&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Rob_35
    Rob_35 Member Posts: 33
    reversing flow direction on a series loop

    I have a series loop fin-tube baseboard zone with oversized radiation on the first part of the loop, and merely adequate radiation on the last part.

    There will be an opportunity during a repipe to swap ends, thus putting the warmer supply water through the adequate rooms first, then the overradiated room last.

    Presently, this loop has a decent delta-T so it would seem there's a benefit to flipping the flow direction.

    Any downside to this? Seems to make sense at first thought.

    Thanks.
  • Rob_35
    Rob_35 Member Posts: 33
    Did it

    Thanks Al. That's the very reason I posed the question. The load calcs for various supply temps vs. ODT say it's a winner.
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Can you split it?

    Intercept the return from the mid-point with a home-run and have two separate zones, one reversed from the original flow direction, the other remaining the same.

    This will dramatically reduce the pressure drop (by 75% if of equal proportions) and give better control/satisfaction to more spaces.

    Just a thought.
  • Rob_35
    Rob_35 Member Posts: 33
    cantilevers, walls, and cabinets, oh my!

    Not easily.... Neat idea, though.