reversing flow direction on a series loop

In principal it should work, but in theory, you should do proper heat loss for each room and determine the need vs. output at design temp. Go figure!

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=248&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Rob_35
    Rob_35 Member Posts: 33
    reversing flow direction on a series loop

    I have a series loop fin-tube baseboard zone with oversized radiation on the first part of the loop, and merely adequate radiation on the last part.

    There will be an opportunity during a repipe to swap ends, thus putting the warmer supply water through the adequate rooms first, then the overradiated room last.

    Presently, this loop has a decent delta-T so it would seem there's a benefit to flipping the flow direction.

    Any downside to this? Seems to make sense at first thought.

    Thanks.
  • Rob_35
    Rob_35 Member Posts: 33
    Did it

    Thanks Al. That's the very reason I posed the question. The load calcs for various supply temps vs. ODT say it's a winner.
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Can you split it?

    Intercept the return from the mid-point with a home-run and have two separate zones, one reversed from the original flow direction, the other remaining the same.

    This will dramatically reduce the pressure drop (by 75% if of equal proportions) and give better control/satisfaction to more spaces.

    Just a thought.
  • Rob_35
    Rob_35 Member Posts: 33
    cantilevers, walls, and cabinets, oh my!

    Not easily.... Neat idea, though.