Better Aquastats?
BillW@honeywell
Member Posts: 1,099
Part number is 107408, comes in a 4 ounce can. As far as protecting your kids from scalding, most new shower valves have automatic anti scald built in, but you also can get whole house 3-way mixing valves that won't allow the water temp above 145. There are undersink versions as well, if you only want one fixture protected. Our Whole-House models are the AM series, NPT, union & sweat models available sizes from 1/2 to 1". Teflon coated moving parts minimize mineral buildup. When you pipe them, run a seperate line of hot water for the dish washer and/or laundry, making sure that the sink isn't on the same line. That way, the dish washer and clothes washer gets the highest temp water, cleaning & sanitizing the dishes better, and saving electricity by not needing auxiliary temperature boost. Check it out at www. customer.honeywell.com
New To Me
Just saw my first electronic aquastat (Honeywell L 7224) by accident; never even knew they existed! I'd like to graduate up to a very accurate aquastat and a very accurate boiler tridicator for all of my jobs. Any opinions?0 -
Beware...
if its used as a final safety device (high limit) it MUST be guaranteed to fail in a safe condition...
Hey work great as controllers and aquastats, but watch out when using them as high limits in critical situmacations...
ME0 -
L7224U
I understand that some of the 7224 models have an adjustable Hi Limit Differential. Does anybody know the maximum differential that can be set? The manual doesn't specify it.
Thanks,
Ron0 -
Aquastats
I have a 60 gal stainless steel, Stor-Ex, hot water storage tank . i changed the aquastat one in 4 yrs. it seems to , at times, go on and off about 5-6 times. I thought that there was a diff?. someone else suggest heat transfer grease which i cant find anywhere. any thoughts?
Heat Transfer paste
I have a dozen jars of the Honeywell heat paste if you are interested.0 -
think it would solve my problem? id appreciate it. But why cant i get it at the supply?0 -
seems to me you got a lousy supply(nm)
Aquastats
more details: i have the aquastat set at 125, dont want the kids getting scalded. Would setting it to 140 stop it from cycling on and off within seconds? secondly, heat trasfer grease: ridgewood plumbing supply doesnt have it.
Aquastats
oh yes and I would put a mixing valve on to temper it back to 125
Limit
usually any MH control that starts with a L is a limit. If it is just a operating control it will start with a T for thermostat. bob0 -
Yikes
4 ounces of MH heat transfer paste in one location is a scary thought. Be REAL careful when you open that sucker cause the whole world is gona turn silver:)0