Zone Valve location question:
Please forgive my ignorance, but I have a question regarding zone valves.
First, there seem to be several opinions on how to stop ghost/gravity flow when a zone isn't calling for heat. Some people belive a swing check should be installed on the return side of each zone, others say to create a thermal trap. It is my understanding that swing checks tend to chatter.
My question is this:
Can I install the zone valves on the RETURN side of a secondary loop and use a TACO 007 with integral flow check on the supply side? Why/Why not?
Thanks and sorry if there is an obvious answer to this question.
  • Sure you can
    but a soft seat spring check would also work, be less expensive, and would not require power to operate. Yes, swing checks, even on a vertical line, tend to be noise makers in hydronic systems.
    Flow check, the weighted type, are another non electric option.
    hot rod
  • I'd choose either method
    Using IFC circs on the supply and zone valves on the return is overkill , in my opinion . We are new to using IFC circs so I'll reserve my opinion about them bypassing . But before them we used either regular Tacos with weighted flowchecks , or zone valves above the system circ on the supply . No check on the return , ever . Never had a problem with heat bypassing , except for crud getting stuck on the flowcheck . And that was one in thousands of zones installed .
  • Just curious, why no flow check on the return? Paul sr.
  • Never needed one there
    The weight in the flowvalve holds the hot water down on the supply side . It's also a flowcheck , stopping flow going in reverse . I've personally seen less than a handful of heat bypass problems , we changed the flowvalve on the supply and stopped the problem right there . I would guess you could get heat up from the return if some radiation is close and higher than the boiler , but I've not seen that happen yet .
  • Primary secondary
    piping adds some different flow dynamics than a basic pumped series piped boiler. Those generally work, without ghost interference :) with only one side protected.
    In primary secondary there are a number of forces trying to rob BTUs from the primary loop. Often unbeknownst to the operator. I would highly recommend protecting both supply and returns on all secondaries piped from a primary loop.
    In this link are some methods shown with pictured examples.
    http://www.pmmag.com/CDA/ArticleInformation/features/BNP__Features__Item/0,2379,13972,00.html
    hot rod