Adding antifreeze to system
piping arrangements,known or unknow volumes,minor technicalities such as that.
  • jrc2905
    jrc2905 Posts: 98
    Adding antifreeze to system.
    Any suggestions for adding antifreeze to a boiler and reducing the amount lost on the purge?
  • jrc2905
    jrc2905 Posts: 98
    just in a general application.
  • Transfer Pump
    Use a transfer pump to circulate a pre-mixed propylene glycol solution. That way there is no loss. A makeup water connection should not be used on a system containing antifreeze.
    -Andrew
  • Dont forget
    That a 30% mixture of glycol will result in a BTU output loss of 15% with a 5% increase in head against the system circulator. A 50% mixture of glycol will result in a BTU output loss of 30% and a 50% increase in head against the system circulator.
    Also, glycol has a different rate of expansion than water, you may need a larger expansion tank, depending on system size.
    Chuck
  • But
    head loss is non-linear.
    According to Dowfrost data, the specific heat is 7.5% less for 104F Dowfrost propylene glycol at 50% versus 30% solution, and approximately 14% less than water.
    -Andrew
  • Leo
    Leo Posts: 772
    Chuck,
    I find this very interesting and have booked marked it. Do you have a reference cause I know I will be argued with.
    Thanks,
    Leo
  • Yes I do,
    The instructions on the anit freeze. I will have to dig them out, and let you know exactly what it says.
    Chuck
  • It may
    have something to do with the make up of Dow vs. the propolyne glycol that I use.
    Chuck