Adding antifreeze to system
RoosterBoy
Member Posts: 459
piping arrangements,known or unknow volumes,minor technicalities such as that.
Adding antifreeze to system.
Any suggestions for adding antifreeze to a boiler and reducing the amount lost on the purge?0 -
just in a general application.0 -
Transfer Pump
Use a transfer pump to circulate a pre-mixed propylene glycol solution. That way there is no loss. A makeup water connection should not be used on a system containing antifreeze.
-Andrew0 -
Dont forget
That a 30% mixture of glycol will result in a BTU output loss of 15% with a 5% increase in head against the system circulator. A 50% mixture of glycol will result in a BTU output loss of 30% and a 50% increase in head against the system circulator.
Also, glycol has a different rate of expansion than water, you may need a larger expansion tank, depending on system size.
Chuck0 -
But
head loss is non-linear.
According to Dowfrost data, the specific heat is 7.5% less for 104F Dowfrost propylene glycol at 50% versus 30% solution, and approximately 14% less than water.
-Andrew0 -
Chuck,
I find this very interesting and have booked marked it. Do you have a reference cause I know I will be argued with.
Thanks,
Leo
Yes I do,
The instructions on the anit freeze. I will have to dig them out, and let you know exactly what it says.
Chuck0 -
It may
have something to do with the make up of Dow vs. the propolyne glycol that I use.
Chuck0