gas heating question
Big Ed
Big Ed Member Posts: 1,117
> i think i'd look for a nail or staple in the wire <BR>
> to the condenser & then look at the <BR>
> t-stat.<BR>
> <BR>
> <BR>
> <BR>
> <BR>
> <BR>
> <BR>
> <BR>
> "oil heats best & always <BR>
> will" <BR>
<BR>
The Y terminals on a board tend to be just a lug and a common for the contactor coil. Not saying the design of the board uses it for other reasons.
I would also check the thermo wire first as Joe posted....Could be a short...
What is odd to me is why the heat works after you disconect the contactor? The only thing I can come up with is the transformer does not have the power to pull in both,the G valve and the contactors coil at the same time.Or the board in design ,if it sensors voltage at Y will shut off the heat.I don't know without reading the scymatic,but both takes us back to a short in the wire.....
  • tech1956
    tech1956 Member Posts: 1
    arcoaire gas furnace
    Found condenser running during call for heat. Heater will not fire consistently unless one side of 2 wire to condenser is pulled from Y terminal on circuit board. Is problem more than likely stat related or circuit board. Thanx
  • joeoilman
    joeoilman Member Posts: 30
    i think i'd look for a nail or staple in the wire to the condenser & then look at the t-stat.
    "oil heats best & always will"
  • What is the make and model
    of the circuit board? Give me that and I can tell you what internal circuits may be giving you trouble.
  • clammy
    clammy Member Posts: 3,242
    T stat sub base
    Check yor condenser wires dis connect them and ohm them out then check your t stat maybe the sub base is bad and i believe on some models you need a good ground for the common termial is made through the cabinet grounding and i have had 1 or 2 do the same i believe mostly on the likes of goodman if not mistaken peace clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ