gas heating question
Big Ed
Member Posts: 1,117
> i think i'd look for a nail or staple in the wire <BR>
> to the condenser & then look at the <BR>
> t-stat.<BR>
> <BR>
> <BR>
> <BR>
> <BR>
> <BR>
> <BR>
> <BR>
> "oil heats best & always <BR>
> will" <BR>
<BR>
The Y terminals on a board tend to be just a lug and a common for the contactor coil. Not saying the design of the board uses it for other reasons.
I would also check the thermo wire first as Joe posted....Could be a short...
What is odd to me is why the heat works after you disconect the contactor? The only thing I can come up with is the transformer does not have the power to pull in both,the G valve and the contactors coil at the same time.Or the board in design ,if it sensors voltage at Y will shut off the heat.I don't know without reading the scymatic,but both takes us back to a short in the wire.....
> to the condenser & then look at the <BR>
> t-stat.<BR>
> <BR>
> <BR>
> <BR>
> <BR>
> <BR>
> <BR>
> <BR>
> "oil heats best & always <BR>
> will" <BR>
<BR>
The Y terminals on a board tend to be just a lug and a common for the contactor coil. Not saying the design of the board uses it for other reasons.
I would also check the thermo wire first as Joe posted....Could be a short...
What is odd to me is why the heat works after you disconect the contactor? The only thing I can come up with is the transformer does not have the power to pull in both,the G valve and the contactors coil at the same time.Or the board in design ,if it sensors voltage at Y will shut off the heat.I don't know without reading the scymatic,but both takes us back to a short in the wire.....
0
Comments
-
arcoaire gas furnace
Found condenser running during call for heat. Heater will not fire consistently unless one side of 2 wire to condenser is pulled from Y terminal on circuit board. Is problem more than likely stat related or circuit board. Thanx0 -
i think i'd look for a nail or staple in the wire to the condenser & then look at the t-stat.
"oil heats best & always will"0 -
What is the make and model
of the circuit board? Give me that and I can tell you what internal circuits may be giving you trouble.0 -
T stat sub base
Check yor condenser wires dis connect them and ohm them out then check your t stat maybe the sub base is bad and i believe on some models you need a good ground for the common termial is made through the cabinet grounding and i have had 1 or 2 do the same i believe mostly on the likes of goodman if not mistaken peace clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements