Revision for the Taco 007 IFC ?
Restrictions should always be avoided on the suction side of a pump. Cavitation may result from restrictions on the suction side. It's basic fluid mechanics. A 007 in a pressurized system may not have issues, but why ask for problems? I'm happy to see they have moved the check valve.
-Andrew
  • After having an IFC
    come through with a missing insert , we broke open a few boxes to see if any others were missing . We found 2 different body styles - one has the check on the discharge of the pump , one has it in the body . Is one of these a newer version of the IFC ? If memory serves , doesn't the 009 and 0011 have the insert in the discharge side ?
  • Al Corelli
    Al Corelli Member Posts: 454
    My Dad says there were some noise issues. Maybe they fixed them? They have been taking out the check valves because of this "noise". I have had NO problems with them, but I do not retrofit them where flow valves exist, and I think that may be where their problem may lie.
    They buy 007s by the skid. A lot.
  • We just started
    using the IFCs , maybe 100 or so installed so far . I haven't noticed any noise issues with the ones we installed - the circulator on the right in the pics . The circ on the left is the new version , I think ?
    Al , has your dad had any heat bypass problems with the IFC ?
  • hr
    hr Member Posts: 6,106
    I applaud Taco's change of heart :)
    in moving the check to it's rightful place. At the discharge side! The notice claims input from the installers in the field lead to the change.
    Nice to know manufactures are willing to listen and adjust, thanks!
    We could have saved you some time, energy, and marketing $$'s
    hot rod
  • Al Corelli
    I'll ask tomorrow.
    I have not had any trouble with 007s.
  • John White
    John White Member Posts: 120
    ifc location change
    taco did recently change the location to the discharge side of the 007. And, yes, <hot Rod, it was absolutely do to the comments from the field installers. Those are the ones who know, far better than us.
    Nice to see a plug from you, Hot Rod. Sort of rare.
    We have had no noise complaints on the 007 ifc.
    John White
  • clammy
    clammy Member Posts: 3,242
    hey ron
    I've install a bunch with the flow check on the inlet and only had 1 promblem one as for noise no complaints .As for heat migration not a promblem and alot where on boiler with tankless coils .The newer version has a smaller gosset i notice in your pics i like that i don,t have to build up the versa bar top keep the gosset off the panel peace clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
  • Joe Mattiello
    Joe Mattiello Member Posts: 748
    Taco changes IFC location on some pumps
    Hello
    You are right some of the IFC models now have the integral flow check located in the discharge flange. For your reference I have included all the models that were changed, and notice a -1 in the nomenclature designating the IFC in the discharge flange. To clear the air the changes were done because of popular demand. Installers prefer the IFC valve on the discharge flange to allow for easier identification and simplified air purging using standard piping and purge valve configuration. To answer your second question, the 009, and the 0011 have the IFC in the volute, and not the discharge side. My perspective on the change of IFC location, shows that Taco is sensitive to their customers needs, and will try to accommodate in most cases, obviously this is one of them.
    Standard 005-F2-1IFC 007-F5-1IFC 008-F6-1IFC
    Priority Zoning 005-ZF2-1IFC 007-ZF5-1IFC 008-ZF6-1IFC
    Variable Reset 005-VRF2-1IFC 007-VRF5-1IFC 008-VRF6-1IFC
    Variable SetPoint 005-VSF2-1IFC 007-VSF5-1IFC 008-VSF6-1IFC
    Variable Voltage 005-VVF2-1IFC 007-VVF5-1IFC 008-VVF6-1IFC
    Taco, Inc.
    Joe Mattiello
    Technical Service Technician
    joemat@taco-hvac.com
    401-942-8000 X 484
    www.taco-hvac.com
    Joe Mattiello
    Taco Comfort Solutions