Refrigeration fittings VS water fittings
Carl PE
Carl PE Member Posts: 203
pm engineer <a href="http://www.pmengineer.com/CDA/ArticleInformation/features/BNP__Features__Item/0,2732,141370,00.html">link</a>
iirc, this guy was trying to sell a "dimpler" tool for the fittings.
  • Refrigeration VS Water Fittings
    We are having a disagreement around here over the differance between refrigation fittings and water fittings.
    I just read an article about how to set a pipe into a water fittings to braze for refrigation. The article talked about not setting it to deep in the socket and talked about a tool make to place a stop in the fitting to keet from setting it to deep. Did anybody see that article and knows where I may find it?
    Does anybody know where I can get info like that?
  • Mitch_4
    Mitch_4 Member Posts: 955
    I would never use
    water fittings in refrigeration. Not made for it. Not dehydrated. not rated for refrigeration. It may not be designed to take the pressure either. (Iheard that once, but not sure of the validity).
    Stcik with refrigeration fittings. keep them seperate, and clean. I use old margarine (5# tub) rubbermaid containers that the wife saves for me. They stack, and seal.
  • Big Ed
    Big Ed Member Posts: 1,117
    interesting
    A brazed connection is a bead around where the fitting and the tubing meet.Where a soldered connection is along the inside of wall of the fitting and tubing.
    Does pulling out the tubing when brazing lowers resistance or prevents a dirt trap?
  • The refrigeration fittings we buy are in boxes (not bags like med gas fitting) so I don't see where having a dehydrated fitting would do much good if it's not bagged.
  • FredR
    FredR Member Posts: 62
    Author: big ed
    Subject: interesting
    "A brazed connection is a bead around where the fitting and the tubing meet.Where a soldered connection is along the inside of wall of the fitting and tubing."
    A properly brazed joint will have the filler material drawn into the fitting socket in the same manner as solder. I personally think brazing is over used, Stay Brite #8 does a very good job with a lot less heat. And I was taught to fully seat the pipe in the fitting. (unless it is a little short) Hmmm!
    IMO, just my 2¢.
  • jim lockard
    jim lockard Member Posts: 1,059
    If only
    they would make propress fittings for ref. work.
  • Boiler Guy
    Boiler Guy Member Posts: 585
    Soon, I'll bet
  • Boiler Guy
    Soon, I'll bet
    Viton O rings ..... lock and load
  • Boiler Guy
    SO.... how do you REALLY tell the difference??
    What is the criteria one would use to determine the difference between AC and water fittings ... for the uniniated helper. I have 3 boxes of 1/4 to 3/4 fittings that even I can't really be sure of the difference. I guess weight would help determine it.
  • Djorn
    Djorn Member Posts: 1
    Fiting difference
    Refrig. fittings are usually long radius fittings, to reduce pressure drop in the lines, while water fittings are usually short radius fittings, since pressure drop is not usually as critical an issue.
  • Mitch_4
    we buy ours
    bagged too..but we'll split some of the lesser used pieces amongst 2-3 guys. Hence the rubbermaid containers.
  • Big Ed
    Stay Brite
    I hear of a few guys using Stay Brite..Do you need to use **** with it ?
    I use the small oxi unit , #15 rod and use a heat sink that comes in a cauk tube.... I have problems around the back of the fitting you can not see. Would be nice if rod would flow
  • jim lockard
    Stay Brite
    I love Stay brite, been useing it for years with no problems. Low tempture will not burn up the valves and fittings like silflos. As for flux Ed I use the Stay Brite brand such as Stay clean. J.Lockard
  • S Ebels
    S Ebels Member Posts: 2,322
    Differences
    Frig fittings are usually longer radius (ells) and from what I understand, are tested to higher pressure. (I don't know this to be a fact) They are sized by the OD of the tubing, thus, a 7/8" refrig fitting fits the same OD tube as a 3/4" plumbing fitting. Same with 5/8" refrig and 1/2" plumbing stuff.
    I have used them interchangably (in a pinch) for years and not had a single problem. I wouldn't see anything wrong with plumbing fittings especially on the vapor side of the system. The caveat here is to be certain the fittings, whichever breed, are clean.
    On the matter of brazing vs soldering, I was taught to braze everything in a refrigeration system and did so for many years. Then one day I came across a spec sheet for Staybrite 8 and I haven't brazed a fitting since. I have never had one let go even on commercial apps. In fact I recall going to look a a condenser we had installed that was on it's 4th summer. It was hotter than the hubs of you know where and the condenser was nearly hidden by long grass and choked off with poplar tree fuzz. The high side showed a pressure of 470 PSI and the poor thing was so hot I thought it would start the grass on fire!!! If that didn't cause the StayBrite to fail I don't know what would.
  • Jim S
    Jim S Member Posts: 82
    unfortunately you can`t use stay-brite with 410-A refrigerant,the lines have to be brazed. it`s not the pressures that are an issue it`s the flux in the system.
  • TGO_54
    TGO_54 Member Posts: 327
    Try using
    Blockade. It is a brazing rod so you have to use high temps, but it will flow more like a solder.
  • Rookie_3
    Rookie_3 Member Posts: 244
    ACR tubing is clean, dehydrated, and seamless. Brazed joints vs. solder.....if you were in a super market or some
    place similar with overhead AC lines knowing that fire turns freon into Fosfeen (Mustard) gas, which would you prefer, a soldered or brazed fitting? 5% silver brazing rod takes 1,100* to melt it and the higher the silver the more temp needed.............ROOKIE
  • Big Ed
    Flux
    I always thought one of the reasons using rod was the fact that you did not need flux .. I thought introduction of flux to the system is adding acid to it. And the acid eats away at the windings ?? Is this incorrect way of thinking??
  • jim lockard
    I set
    the pipe half way in the fitting then flux. Ed I try not to over flux the fitting. Most compressor bearing equipment today has dryers built in or added. Think more equipment fails from poor evaction then flux. IMHO Best Wishes J.Lockard
  • jim lockard
    The Smoke
    From the 600 degree packaging burning, will get you long before the phogene gas will. Best Wishes J.Lockard
  • Scott Kneeland
    Scott Kneeland Member Posts: 158
    staybrite 8 vs brazing
    I have used both with no problem. I have used staybrite 8 in tight spots and attic jobs on R22 where the less fire the better. I do mostly Trane systems so the R410a is common, for this you must braze all joints. I have always used a small oxy/acetelene torch to braze it heats up much quicker with a smaller tip and helps stop the overheating of the surounding area. Good evacuation is the most important part, USE A MICRON GAUGE.
    Question for thoes guys using Staybrite8 do you only flux the male fitting? I do and was taught this way. is it correct?
  • Rookie_3
    Hey Jim, Good point!! Never thought of the packaging.(PVC)
    ROOKIE
  • Paul P
    Paul P Member Posts: 5
    what about the nitrogen
    all this talk about brazing and soldering. Do you run nitrogen when using the stay bright?
  • freon12
    freon12 Member Posts: 15
    flux
    I've been in refrigeration for over 20 years and for my 2cents this is the way we braze.....
    Copper to Copper - no flux 5% to 15 % rod
    Copper to brass - staybrite flux 5% to 15 % rod
    Copper to Steel - staybrite flux 45% silver solder
    Copper to Steel - 2nd option staystill and brass rod dipped into soldering flux w/ staybrite on fittings
    This might sound funny but it took me a few months to actually solder water lines, I always ran the torch to hot, to me it was actually hard to solder as opposed to braze...The 1st few years that I was doing water lines I was actually taking the valves apart and brazing water lines :D
    To me solder was so flimsey and weak compared to brazing....
    have fun
  • freon12
    nitrogen
    The purpose of the nitrogen is this
    When brazing pipes toghter in large systems you trickle nitrogen threw the system to limit the amount of "slag" inside the pipes.
    Slag: basically a flacky substance that is like a dust, I think its actually carbon but not sure....
  • S Ebels
    And......
    The nitrogen is used to prevent oxidation of the tubing due to the high heat required with brazing (1100*+) When you braze you are actually melting the tube and the filler material together. At temps in this range the copper will begin to "burn" or oxidize. Purging the tube with nitrogen eliminates the problem because oxidation cannot occur without oxygen.
    Not so with soldering. The temps don't go high enough to cause internal oxidation of the pipe. Therefore, no flakes. If I'm not mistaken Solderene flux is non acid base.
  • jim lockard
    scott
    I only flux the male part of the fitting