direct vent clearances
Scott Denny
Scott Denny Member Posts: 124
"I do not understand why people insist on venting appliances under decks, but apparently there is much I do not understand!"
Jack, you understand just fine.
"If it walks like a duck and talks like a duck, it's a duck."
Or as Forest would say, "Stupid is as stupid does".
  • clammy
    clammy Member Posts: 3,242
    Direct vent clearances
    I,ve looked in the installation book and i usually wouldn't even think of doing it but what are the codes for direct vent wall hung hot water heaters and clearances for above the termatation ,like a deck above about 2 feet above and a active patio in the same area i didn't sell the unit nor mount it to the wall besides the gas line being a little issue 60 feet 1 " pipe with boiler dryer stove and grill on it .The input for the unit was 29,000 to 194,000 the unit was a noric made in japan model #n-069m .They have a tankless coil on a 27 year old gas hot water boiler and seem to be money tight i was stucked into this one and would rather not get involved but i'll maybe give them a install price but am disliking the original plumbers location and choice since he wouldn't return to finish or start the install .PS the plumber is there son whea ? thanks in advance clammy peace
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Mosherd1
  • jim sokolovic_3
    jim sokolovic_3 Member Posts: 5
    The code only states that...
    the vent shall not be installed below eaves or parapets (?), or over an area where condensate or vapor could create a nuisance or hazard. The manufacturer's instructions should embellish on this further, and must be followed by code also. In this case, flue gas bypass back into the air intake, and freezing of condensate on the above deck surfaces is very much a safety concern. Hope this helps.
  • Michal
    Michal Member Posts: 213
    There are code restrictions
    depending on the state you are in, you might have to be
    10'-0" away from a window, etc. Look into the state code book, they will tell you what the clearences are.
  • Steve_35
    Steve_35 Member Posts: 545
    Why is the required distance from an operable window or door
    4' horizontal or below if you pull combustion air from inside the building but only 12" if you pull the combustion air from outside?
  • jim sokolovic_3
    Perhaps it's assumed...
    that a direct vent appliance has an adequate supply of combustion air piped directly to it - and therefore is less likely to produce CO than an appliance that relies on an adequate supply of combustion air from the inside of the building?
  • jim sokolovic_3
    And also the National Feul Gas Code...
    allows the vent terminal on a Direct Vent appliance with an input less than 50,000 BTUH to be within 9" of an opening to the building. You really have to wonder how someone figured you could be 3" closer to an opening at the lower input - the 12" distance already defies common sense, to me. I was also wondering if they assume the Direct Vent appliance won't create a negative pressure in the building (on it's own) that might suck the flue products back into the building?
  • Jack_29
    Jack_29 Member Posts: 2
    Vent Clearances for DV's
    NFPA 54 says that a dv in excess of 50k input must terminate at least 12" from an opening in the building. Rinnai water heaters, which I am most familiar with require a min 3ft below an overhang, eve, etc. I think that a good rule. I do not understand why people insist on venting appliances under decks, but apparently there is much I do not understand!
  • Jack_29
    The principle of DV's is
    That of a "balanced flue" and "sealed combustion". Only the amount of air necessary to support proper combustion is taken into the unit and then exhausted as flue gas. Therefore the combustion process will not create a negative pressure in the building as it is isolated from the building atmosphere. Pressure neutral!
  • Bob Harper
    Bob Harper Member Posts: 1,143
    interpreting clearances
    Contact the mfr if the application does not fit what is listed in the instruction manual. In this case, if the deck or patio cause enough restriction of airflow around the termination, it may not be allowed. Aside from stated clearances, it must breathe. For instance, certain appliances can vent out onto a porch covered by a deck as long as they're open on at least 2 sides. However, if the porch is screened, it is not allowed.