parallel boilers to a steam main
don p
Member Posts: 1
What is the correct connection for parallel steam boilers to an overhead horizontal steam main? The steam connection from these boilers connect to the bottom of the main. Seems like they should connect to the top or sides so condensate won't drain into one or the other when only one is operating.
Well, on the big stuff...
.... a.k.a. the Weil Mclain LGB series, the installation manual shows dropped headers when connecting multiple LGB's to a steam main. I think your theory re: doing this to keep the condensate from flowing back unevenly is right on the money. Have a look at the Weil McLain site, you can download the installation manual there.0 -
Ooops!~
A picture is worth......
ALOT! Here is a Slantfin modular setup. They use a common header and Hartford loop then feed up to the steam main. Other setups use seperate headers and Hartfords(or equalizers) for each boiler.
Boilerpro0 -
false water line
If i'm correct in what i'm seeing is that not a false water line that you have built there excellent work peace clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Yep , the best way to go would be dropping down
in to the main. Mad Dog
Actually, no....
it is a manifold off the equalizer for the maual reset LWCO and the operating LWCO. The bottom is tied below the water line and the topaove the water line on the equalizer. Iplan on getting pics of the final completed installation when I get a chance. Haven't done one of those yet.....someday though.
Boilerpro0
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 162 Indoor-Air Quality
- 71 Pipe Deterioration
- 999 Plumbing
- 393 Solar
- 55 Water Quality
- 46 Industry Classes
