HARTFORD LOOP
hph
hph Member Posts: 4
WHAT IS THE PROPER HEIGHT FOR CONDENSATE TO RETURN TO BOILER THROUGH THE HARTFORD LOOP. ALSO DOES IT WORK BETTER TO COME STRAIHGT UP AND INTO THE SUPPLY MAIN FROM THE STEAM BOILER OR 90 OVER AND UP
  • hph
    hph Member Posts: 4
    STEAM
  • Al Letellier
    Al Letellier Member Posts: 781
    hartford loop
    The connection point of the hartford loop into the equalizer is commonly 2" below the normal water line of the boiler. I'm not sure I understand the second part of your question. But if I get it right, it doesn't matter how you get the steam from the boiler to the main as long as you don't reduce the boiler size of the pipe. Always pipe the riser full size from the boiler. By 90* up and over, do you mean a drop header? Always best this way on larger boilers with multiple risers. It makes piping easier and give drier steam, in general.
  • Biged
    Biged Member Posts: 117
    Hartford loop
    when you come up (min 24") then 90, then go up to the main