HARTFORD LOOP
hph
Member Posts: 4
WHAT IS THE PROPER HEIGHT FOR CONDENSATE TO RETURN TO BOILER THROUGH THE HARTFORD LOOP. ALSO DOES IT WORK BETTER TO COME STRAIHGT UP AND INTO THE SUPPLY MAIN FROM THE STEAM BOILER OR 90 OVER AND UP
STEAM
WHAT IS THE PROPER HEIGHT FOR CONDENSATE TO RETURN TO BOILER THROUGH THE HARTFORD LOOP. ALSO DOES IT WORK BETTER TO COME STRAIHGT UP AND INTO THE SUPPLY MAIN FROM THE STEAM BOILER OR 90 OVER AND UP0 -
hartford loop
The connection point of the hartford loop into the equalizer is commonly 2" below the normal water line of the boiler. I'm not sure I understand the second part of your question. But if I get it right, it doesn't matter how you get the steam from the boiler to the main as long as you don't reduce the boiler size of the pipe. Always pipe the riser full size from the boiler. By 90* up and over, do you mean a drop header? Always best this way on larger boilers with multiple risers. It makes piping easier and give drier steam, in general.
Hartford loop
when you come up (min 24") then 90, then go up to the main0