hot water recirculating pipe
bwinn
bwinn Member Posts: 2
how do i pipe a recirculating pipe from the hot water tank. where can i get the information.
  • bwinn
    recirculating
  • Joe Mattiello
    Joe Mattiello Member Posts: 748
    Taco, recirulation pump 003-PNP
    Attached is an instruction sheet, and submittal data information for the Taco, 003 plumb & Plug, with a timer, and 6 ft pig tail to facilitate wiring. The instruction sheet has a diagram of a typical piping layout.
    Taco, Inc.
    Joe Mattiello
    Technical Service Technician
    joemat@taco-hvac.com
    401-942-8000 X 484
    www.taco-hvac.com
    Joe Mattiello
    Taco Comfort Solutions
  • grindog
    grindog Member Posts: 121
    hot water recirc
    When you pipe a hot water recirc you must put a check valve on cold water inlet, I usually use a taco 006 bronze circulator and wire it with out an aquastat so the circulator runs continuously. some guys like to use an aquastat. it has been a while since i have done one the only other thing is an expansion tank i was told to always put one in but recently a contractor friend told me you dont need one the water heater acts as the expansion tank. hope i could help
  • Uni R
    Uni R Member Posts: 663
    Ummm
    The only way that water heater will help alleviate expansion is to leave it shut off. Your contractor friend's advice is bad.
  • Weezbo
    Weezbo Member Posts: 6,231
    i like the 004 1/2.....
    now the 003 well it is a small miricale that i have even 006 1/2" ...getting a 003 now That would be trick :) ......run back from th 'T' from the furthest fixture tie the line into the cold water supply to the water heater of your choise put a check on both the hot (recirc) and the cold. cut a 'T' in for an st- 12 or st-15 on the cold water ....good day :)
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,011
    Try...
    ...www.gothotwater.com . You don't need a separate recirc line at all.
    Yours, Larry
  • Gordy
    Gordy Member Posts: 9,546
    Expansion tank
    Oh it (water heater) will act as an expansion tank alright. As it crushes the flue pipe.
  • hr
    hr Member Posts: 6,106
    Gdog
    I suspect what you friend meant was the well trol tank may act as an expension tank?
    If you are on a well system and there are no checks between the well tank and HW tank.
    hot rod
  • grindog
    expansion tank
    I called him after i posted that message and we discussed it further he was wrong with his theory and i was right sorry gor the false info