ed wallace
Member Posts: 1,612
was on a job today customer wants to move a bryant 90 plus gas furnace according to manufacturers info in order to move the furnace the minimum vent size with 6 elbows is 2 1/2 in. pvc customer says well the original installers used 1 1/2in. pvc so it should not be a problem i say it should be at a minimum 3 in. pvc so i am seeking advice
0
Comments
-
Go by
Go by the book. If they specify a minimum of 2 1/2 so be it. That's the minimum. The gas supplier will probably red tag it if you go smaller anyway. So save the headache. Wouldn't think one inch would make that big of a difference anyway...Good luck..0 -
Is it really 1 1/2" pipe now ? most are 2" minimum. 2 1/2" pipe and fitttings aren't all that common but if thats what the chart calls for it should be at least 2 1/2 3" wouldn't hurt any. Actually have repiped several bryants and carriers due to people pushing the envelope with 2" pipe. Give them 2 prices one to do it right the first time and another to do it twice
0
This discussion has been closed.
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements