Steam boiler water level problem
RonNE
RonNE Member Posts: 7
Having a problem w/ an old steam boiler, water level keeps rising w/ feeder on and drops too low w/in a couple of days if shut off. Not leaking by nor is bypass. The tankless coil has been disconnected back along. The piping is all visable, only a couple of small drips near boiler. Now this is about a 30 year old boiler that we are going to replace in the spring I just need to keep it going for now with a proper water level. There isnt any equalizer nor Hartford loop on the boiler and its the first time I have seen one piped this way, simply returns into bottom of boiler, and w/o check valve. Could this be causing water level problem, hard to believe so with the age of system, not sure? Thanks for replies
  • Barbarossa
    Barbarossa Member Posts: 89
    Your water level
    First guess is the differential pressure can be pushing the boiler water back into the return then the feeder adds more. Eventually a overfill is evident.
  • Check for a restriction
    in the feed water piping where it enters the return. It's possible the unit is feeding when required & w/ a restriction, the pressure on both sides of the V&S equalize and holds the seat open. A broken union test won't show this one.