Steam boiler water level problem
RonNE
Member Posts: 7
Having a problem w/ an old steam boiler, water level keeps rising w/ feeder on and drops too low w/in a couple of days if shut off. Not leaking by nor is bypass. The tankless coil has been disconnected back along. The piping is all visable, only a couple of small drips near boiler. Now this is about a 30 year old boiler that we are going to replace in the spring I just need to keep it going for now with a proper water level. There isnt any equalizer nor Hartford loop on the boiler and its the first time I have seen one piped this way, simply returns into bottom of boiler, and w/o check valve. Could this be causing water level problem, hard to believe so with the age of system, not sure? Thanks for replies
0
Comments
-
Your water level
First guess is the differential pressure can be pushing the boiler water back into the return then the feeder adds more. Eventually a overfill is evident.0 -
Check for a restriction
in the feed water piping where it enters the return. It's possible the unit is feeding when required & w/ a restriction, the pressure on both sides of the V&S equalize and holds the seat open. A broken union test won't show this one.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements