munchkin 199m will not run when tt is put together does dhw
together and I have a coustomer with no heat for two days in the NW I have called htp several times but no response from them may area rep is out of town or atleast has not responded to messages I need any and all suggestions
  • Constantin
    Constantin Member Posts: 3,796
    Ummm...
    When I was at HTP, the reps were busy taking calls, etc. Did you call during business hours? They are on the east coast and as such may close earlier than you expect. More importantly, are there any fault codes that come up?
    One would think that the programming of the Vision 1 must have been messed up if all electrical connections and sensors are OK. You checked them, right?
    I am not familiar with programming a Vision 1 controller or a Munchkin, but I wonder if disconnecting it would prompt the Munchkin into accepting a dry contact across the TT terminal. This in turn would indicate a problem with the Vision 1 programming, not the boiler. Have you taken a Vision 1 class and are you certified to set a Munchkin up?
    I would also examine whether the pump for the Munchkin and the primary loop pumps are operational. You did pipe it according to the HTP diagrams, right? From what I have been told, Munchkins like their piping done the HTP way...
    And now I'll let the real experts chime in. Cheers!
  • chuck shaw
    chuck shaw Member Posts: 584
    It is most likely a
    programming error.
    Go into your vision contol, and make sure that the first step is "de". Not "di" or "do".
    Hope this helps,
    Chuck Shaw
  • bill Fuller
    bill Fuller Member Posts: 6
    munchkin 199m with Vision 1 not heating
    Yes I am proud to say that I am a Vision certified installer so far just 1 and 3 but in this case yes I am certified. I have piped it according to HTP's practices, so much so that it looks just like one of the picture that Dan had drawn for them. During power up/test mode it does cycle the boiler pump and system pump, it does not show any faults except when the TT's hit the boiler housing then I get a FOO which is quite common with a low voltage short or grounding. how ever I will give it a try and disconnect the vision package today and see what will happen. I have double checked and had another service tech double check my wiring. and I did call HTP during regular buisness hours 4AM to 8AM mountain time and after sitting in the holding pattern after fifteen minutes it would dump me into the voice mail where I would leave another message. I have left messages all over the place from 10Pm to 10AM and yet no response other than the customer wanting to get mad at me
  • bill Fuller
    munkin fist step is de
    > programming error.
    > "di" or "do".
    > Hope this helps,
    > Chuck Shaw
  • chuck shaw
    Bill
    what extension did you leave the messages at? I never recieved one on my voice mail.
    Chuck Shaw
  • chuck shaw
    try disconnecting your outdoor sensor
    chuck
  • chuck shaw
    bill
    please check your e-mail
    Chuck
  • bill Fuller
    I did disconnect the the out door sensor and EL is kinda slow in
    response for E-mail and as for messages I left them on the diverted Email and the one that states it is the HTP phone
  • chuck shaw
    ok,
    as soon as you get the e-mail I just sent you give me a call, it has my home phone number on it.