  • Dan_15
    Dan_15 Member Posts: 388
    Header size

    The supply and return headers should be mirror images of each other. This helps with delta T, flow rate, less head and MOST IMPORTANT - Dan says so! ("Pumping Away" page 95).
    The use of the reducer/diffuser bushing on the G115 adds less than .012 feet of head because of the very short distance of the fitting.

    Installation of a boiler, near boiler piping, wiring is as individual as each person. There are some contractors who go to great lengths to "create a work of art" when installing a boiler. Most home owners do not care what it looks like as long as it works. Many of the contractors who post here do the installation and the service, so they keep that in mind.

    Will this system operate - yes. Is it as service friendly as we would all like to see at 2am on a no heat call - maybe not. I suggest having it inspected to be sure local code is followed, change the DHW line to one inch by cutting in before the header, as suggested earlier, or add on to the end of the header, Keep return same size as supply up till the boiler.
    Thanks,
  • Bill_39
    Bill_39 Member Posts: 69
    sorry roosterboy

    That was very mean and I shouldn't have posted it. I don't hate you I was trying to make a point that cheaper is not always better. I should just mind my own business. Sorry again.
  • Steve_35
    Steve_35 Member Posts: 545
    What Dan is talking about

    > The supply and return headers should be mirror

    > images of each other. This helps with delta T,

    > flow rate, less head and MOST IMPORTANT - Dan

    > says so! ("Pumping Away" page 95).


    What Dan is talking about there is if you reduce the size of the supply manifold to reflect the decreasing load the manifold will carry as the water gets further down the manifold you will make the return the mirror image of the supply because the sizes the supply manifold was made of were determined by the load at that point. If 1" is all that's required then running a pipe larger on the supply or the retrun really doesn't make any difference.
  • Steve_35
    Steve_35 Member Posts: 545
    How close

    is the vent piping to combustibles?
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    so when...

    piping the 115 do you (Buderus) recommend increasing to 1 1/4" as soon as you get out of the return? kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Larry_10
    Larry_10 Member Posts: 127


    yea so what I have to do is take that reducer I have on my return manifold and stick it directly on the back of the boilers return

    then pipe 1/1/4 from there

    good thing you guys told me this

    thanks
  • Ron Schroeder_4
    Ron Schroeder_4 Member Posts: 46
    Mirrored Manifolds

    > > The supply and return headers should be

    > mirror _BR_ > images of each other. This

    > helps with delta T, _BR_ > flow rate, less

    > head and MOST IMPORTANT - Dan _BR_ > says so!

    > ("Pumping Away" page 95)._BR_

    >

    > What Dan is

    > talking about there is if you reduce the size of

    > the supply manifold to reflect the decreasing

    > load the manifold will carry as the water gets

    > further down the manifold you will make the

    > return the mirror image of the supply because the

    > sizes the supply manifold was made of were

    > determined by the load at that point. If 1" is

    > all that's required then running a pipe larger on

    > the supply or the retrun really doesn't make any

    > difference.




    I think that what Joe (and Dan) were refering to is reverse return. That will equalize the pressure drop in constant diameter manifolds.

    With a properly designed manifold pair that reduces toward the end (or oversized manifold headers), you dont need to make them mirror images (reverse return).

    Ron
  • Ron Schroeder_4
    Ron Schroeder_4 Member Posts: 46


    Hi Roosterboy,

    You could do that or even better might be to replace the first 90 by the boiler return and replace it with a Tee and run the new branch as directly as possable to the indirect return.

    Since you have a horizontal indirect, flow rate is important not only for recovery but also to purge air out of the heat exchanger loops in the indirect tank. (Been there, Done that, Got the T-shirt)

    I would really try to get the Spirovent in main supply and Tee off after it, one leg to the manifold and the other leg to the indirect circ.

    Ron
  • Larry_10
    Larry_10 Member Posts: 127


    > hay guys my boiler is done can anyone tell me

    > what's wrong with it on the supply header from

    > left to right

    >

    > the first 007 is my dhw the

    > next is my hydro air the next is my

    > baseboard

    >

    > this is a buderus g115 28 with lt

    > 160 42gl dhw tank and r 2109 controller power

    > vented

    >

    > the company that did this install is a

    > 80% service and 20% install and you can tell by

    > the no so nice looking install

    >

    > I tried to get

    > them to do it neat I made the board and painted

    > it and laid it out but they changed things on me

    > left scags on my solder joints also I think my

    > dhw should have been copper piped with 1 inch

    > copper instead 3/4 from the taco 007

    >

    > but

    > please let me know if anything should be repiped

    > or changed

    >

    > thanks



  • Brett  O'Connor
    Brett O'Connor Member Posts: 22


    Here is a boiler room Schematic hope this helps.
  • Ted_9
    Ted_9 Member Posts: 1,718


    Brett, how do you make those images?


    PATRIOT HEATING & COOLING, INC.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Brett  O'Connor
    Brett O'Connor Member Posts: 22
    Ted

    I use on this drawing just a basic Visio. You can create drawing that you save as stencils (pumps, styles of boiler, ect..). I have a library of around 2,000 boiler, electrical, mechanical fittings, ect... I then created Templates of applications and then as the design of the job dictates change the template to fit the job. You can create very detailed drawings. For commercial jobs I use a 3-D auto cad based program to draw to scale. There both great tools to use in the field and also to sell the job to the home owner. Here is another example of the new Buderus intall with the GB-142.
  • Steve_35
    Steve_35 Member Posts: 545
    Very Nice

    I can see I've got to look into Visio more. Where did you get the library of "pieces"?
  • Ted_9
    Ted_9 Member Posts: 1,718


    I just did some searching. I found the program and I also found sites where you can download different symbol etc..

    But Brett, do you mean to say that you make the Buderus or boiler images?

    PATRIOT HEATING & COOLING, INC.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Larry_10
    Larry_10 Member Posts: 127


    thanks very much guys the job was all redone and works better and looks better I will post new update pictures tomorrow and thank you all for helping me on this without you id have dirty water and a not so good boiler setup so thanks allot.
    I love this website and the people here im here everyday. I got so into heating that I am now saving money to go to school for it.

    thanks
  • Joe@buderus
    Joe@buderus Member Posts: 165
    Viso Images

    I have Viso at work and have done many drawings for Buderus. E-mail me at jkennard@buderus.net and I can send drawings (got a great "new" image of the GB142 from our rep Steve Grady) that have great images of Buderus products.
    Thanks,
    Joe
  • Brett  O'Connor
    Brett O'Connor Member Posts: 22
    Joe and Ted

    Joe I have made all detailed drawing on the new GB and all Buderus products if you need anymore stencils. I am the rep out in Washington State. Ted email me your address and I would be more than happy to burn a CD of my library and send it your way. No use redrawing these images if the work has already been done. brett@mechagents.com
  • Joe@buderus
    Joe@buderus Member Posts: 165


    Hi Brett! I will be in touch with you on Monday. Please don't send me the picture of Ralph!!!
    Thanks,