main vent sizing & location
Hitzkup
Member Posts: 63
i have a 2" main 40' long the current main vent is a hoffman 45 & it's located at the end of the main right on the elbow with no nipple.
is annyone out there who could help with the proper main vent/vents and where to install it. i'm thinking of a street elbow a 15" nipple another elbow and a 8" nipple will this work?
mark s
mark s
This was my reply to your e-mail
Mark, that piping arrangement will work fine. The only thing I'd change is to substitute a regular elbow and a short nipple for the street elbow. This will not restrict the flow of condensate back thru the elbow like a street ell can. And make sure that the pipes have a slight pitch back to the steam main so condensate can drain properly.
Add a tee, an elbow and a couple of short nipples to the very top, as you want to vent that main with two Gorton #1 or Hoffman #75 vents. Both vents must be mounted vertically.
Hope this helps.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Consulting0 -
thanks
thanks mr. steamhead for your help.
happy new year.
mark s0