main vent sizing & location
Hitzkup
Hitzkup Member Posts: 63
i have a 2" main 40' long the current main vent is a hoffman 45 & it's located at the end of the main right on the elbow with no nipple.
is annyone out there who could help with the proper main vent/vents and where to install it. i'm thinking of a street elbow a 15" nipple another elbow and a 8" nipple will this work?
mark s
    Steamhead Member Posts: 18,211
    This was my reply to your e-mail
    Mark, that piping arrangement will work fine. The only thing I'd change is to substitute a regular elbow and a short nipple for the street elbow. This will not restrict the flow of condensate back thru the elbow like a street ell can. And make sure that the pipes have a slight pitch back to the steam main so condensate can drain properly.
    Add a tee, an elbow and a couple of short nipples to the very top, as you want to vent that main with two Gorton #1 or Hoffman #75 vents. Both vents must be mounted vertically.
    Hope this helps.
    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Oil & Gas Burner Service
    Consulting
  • Hitzkup
    thanks
    thanks mr. steamhead for your help.
    happy new year.
    mark s