P/S V/S INJ
eleft_4
eleft_4 Member Posts: 509
An old friend will be laid to rest...GE must go.
Dunkirk, Beckett and P/S V/S Injection will nurse the monoflo CI rad's!
The unit in pics will be mounted under floor joists.
al
  • hr
    hr Member Posts: 6,106
    nice fab work!
    Any way to get a globe valve in the injection loop for better adjust-ability? Depending on your load you may have to throttle away a bit of that pumps capacity.
    You may also need a check valve in that injection bridge. Use a Grundfos with the intergral check valve for ease of install. Pump away my friend :)
    hot rod
  • eleft_4
    hot rod
    Thanks HR,
    I am using flow check valves on both return and supply of the secondary.
    The ball valve works fine on my radiant system to throttle back, to ramp up the pump. It does take a little tweaking.
    I don't like to use up the basement for a lot of plumbing. (G)
    al
  • eleft_4
    Some good info and formulas article
    I have that one & more of John's articles.
    Thanks HR,
    al
    All tested and ready to hang.
  • eleft_4
    How will it be installed?
    It will be mounted on the floor joists above the boiler. You are looking at the bottom of the unit. The 1 1/4" unions (left in photo, pointing up, will be pointing down) connect to the boiler, the closest is the return. The 2" section on the left side of the photo is the primary. The primary pump is mounted on the boiler return. No pumping away, I am keeping the original compression tank.
    The pump isolator and the temp ball valve on the 11/2" section, (secondary} right side, are return and supply for the monoflo (1 1/4") and baseboard (1") wings of the house.
    Comments or questions? Appreciated,
    al
  • eleft_4
  • eleft_4
    Retiring after 59 years of service.
    I can't push it under the stairs.
    Any one want it? Must pick up at it's location. (G)
    Free...
    al
  • Ron Schroeder_2
    Ron Schroeder_2 Member Posts: 176
    Is that a B&G isolation flange on the injection pump? The other pump looks like it has Webstone flanges.
    Ron
  • eleft_4
    B&G?
    Yes Ron,
    My supplier has B&G for 1" isolator and Webstone for all others including isolator purge 1" ????
    I like the B&G 360 flange feature nicely machined also.
    al
  • Mike Kraft_2
    Mike Kraft_2 Member Posts: 400
    Beautiful Al!
    Being retired does have it's advantages I see.You get to putz around doing what you like.I must admit losing the GE is a bit of a downer.
    I must agree with hot rod...........your injection should have a flow check and also the point with the globe valves.I'm sure you'll manage fine with the BV's.I know you've been around the block several times with it.Very nice clean fabricating.Proud papa.
    cheese
  • eleft_4
    I love to putz
    Thanks Cheese,
    Never stop learning, knowing and not doing is not knowing.
    I wake up with ideas, hydronic ones that is.
    There are days I don't know what I did but time sure fly's!
    al
  • Ken_8
    Ken_8 Member Posts: 1,640
    Al,
    I forget where you live. A few folks I know may be interested in this G.E. - if it has the original compressor. Do you know why it is being removed?
  • eleft_4
    Ken
    Hi Ken,
    It was converted to Carlin years ago. It functions well it is in good physical contrition. I need to get better efficiency @ current oil prices. It has been heating the atmosphere for close to 60 yrs.
    Time to change, it's in one of my rentals. I'm in southern CT. I will be glad to load on your truck.
    I'm looking forward to Minnesota.
    I will email you on my current stats
    al
  • Ron Schroeder_3
    Ron Schroeder_3 Member Posts: 254
    Hi Al,
    I have been wanting to use the B&G iso flanges for the rotating flange since I often use UPS15-58FC pumps that are 90 degrees rotated from TACO. No worries if I have to swap in a TACO on a horizontal run. Unfortunatly I haven't found them in stock anywhere. All of the good stuff is so hard to find, TACO ESP valves, Caleffi ect.
    Ron
  • eleft_4