need advise on old abc oil burner
need specs on p 535 wiel mclain with an abc burner in it. the fire is too long and smoky. does anyone have these specs or advise on how to shorten the flame and dial this fire in by eye and feel
  • S Ebels
    S Ebels Member Posts: 2,322
    Could be a number of things
    All of which need professional attention.
    Your boiler could be sooted up and partially plugged. I'd check this first. When was the last time it was cleaned, as in brushed and vac'd? If it's been loinger than 2 years it needs to be done. Period.
    The burner could have the wrong nozzle in it. The firing rate should be on the label.
    The air adjustment could be off. This is something that is best done by a tech with a combustion analyzer to get it set right.
  • richpoirier
    richpoirier Member Posts: 10
    hi thanks for the get back, the boiler is clean and the nozell is corect, i feel as thoiug the draw asembly is not set properly. it one of those guns that has an adjustable setting form the tip of the nozzel to the end of the blast tube.
    Steamhead Member Posts: 17,767
    See my answer
    in your other post. The info you need shouldn't be hard to find.
    Consulting
  • 45CU-1 ABC
    in the Weil 535. 1.25 X 80 W Nozzle @ 100#. Air Choke Ring Dia 2 5/8". Static Disc Dia 3 13/16". Spinner O/S Dia 2 1/4". Face of nozzle 7/8" back from front edge of Air Choke. Spinner 3/16" ahead of nozzle face. Electrodes 3/8" up-5/8" ahead of NOZZLE ADAPTER FACE-3/32" gap.
    The 535 w/ the ABC was a tough nut. The 2 1/4" Spinner was used only on the burner for the 535. The 35 was also chamberless. Not even a rug. A rug and target wall solved many problems w/ this combo. Good luck.
    By the way. My literature is dated 1971. Nuff said.
  • joel_21
    joel_21 Member Posts: 16
    My solution
    get out your wrenches, remove burner, proceed to nearest dumpster....
  • sootmonkey
    sootmonkey Member Posts: 158
    joel
    joel gets the thumbs up tonight.
  • J.C.A._3
    J.C.A._3 Member Posts: 2,980
    I agree!
  • ed wallace
    ed wallace Member Posts: 1,612
    abc
    reminds me of a lady in waltham ma i delt with yesterday the oil burners were installed in 1957 she wants to nurse them threw this winter my reply good luck
  • richpoirier
    IVE TRIED THE DUMPSTER ROUTINE BUT THIS BOILER IS IN GREAT CONDITION AND I WOULD LOVE TO GET THIS GUN RUNNING OR FIND A SUTABLE WAY TO CONVERT TO A BECKET. ANY IDEAS ON A SUITABLE WAY TO MOUNT A BECKET IN THIS PIG. SOME ONE PUT A CALIN NOZZEL TURBULATOR ON GUN, IT WONT SET UP.
  • ed wallace
    old sunray
    mounting a beckett in it is not a hard thing if you know what you are doing call for help
