Flue adjustment ?
Joe.G
Joe.G Member Posts: 213
Hi, I was wondering, on my new flue pipe there is a weight adjustment, I was wondering how should this be adjusted? Should hte flue be open the hole time the boiler is running? or only at start up, any info would be great thanks.
  • Firedragon_4
    Firedragon_4 Member Posts: 1,434
    It should only be adjusted with
    a draft gauge or manometer by a professional!
  • Joe.G
    Is there a way to get it close?
  • oil-2-4-6-gas
    oil-2-4-6-gas Member Posts: 641
    there are many things that you can screw up by playing with the draft regulator---its not a toy if you don't have instruments leave it alone//// if its noisy or you get a small amount of soot from it you may have a problem---changing the adjustments will not fix whatever problem you might be having it will more than likely cause more problems--
  • Joe.G
    I had a boiler installed, i then replaced all of the piping going out to my chimney inculding the flue The flue door stays open the whole time the boile ris running, i was just wondering where I want it to be, what can happen if it is not adjusted right.
  • Boston Boiler
    Boston Boiler Member Posts: 70
    > adjusted right.
  • oil-2-4-6-gas
    you want it to be maintaining a minimum draft --of ----whatever the manufacturer of the boiler/burner package recommends --you need to know what the overfire draft is supposed to be ----problems can include burning up the diffuser,blast tube,overheating the nozzle can cause sooting ,plugging the boiler destroying the fiber combustion chamber -------------you need to know what you're overfire draft is supposed to be --the chimney draft should be at 1 in water column higher than that and the regulator maintains you overfire draft through the seasons
  • jim sokolovic
    jim sokolovic Member Posts: 439
    Isn't a typical chimney draft...
    about -.06", and a typical over-fire draft -.02" on oil boilers? Of course it varies, but where do you see 1"?
  • oil-2-4-6-gas
    that would be a "difference" of .01 w.c. and overfire depends on the burner boiler combo--- mine is recommended minimum of .03 overfire
  • jim sokolovic
    Just trying to confirm...
    some typical readings you guys see in the field. Is it that unusual to see -.02" over the fire, -.04" in the flue (before the draft regulator), and -.06" in the stack (after the draft regulator, essentially the chimney reading). Am I not remembering things correctly?
  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    Ahhhhh
    .06 AFTER the draft regulator. Thought you meant before.
    We typically see -.02 to -.03 before.
    Mark H
  • jim sokolovic
    That's why I prefer...
    to confine the designation "flue" to the areas before the regulator (or hood), and the designation "stack" to the areas after the regulator (or hood). I know I'm pretty much alone on that thought (here, at least) - but how many times do you hear the flue draft reading being given as the chimney draft reading - they are not the same!
  • Joe.G
    I have no idea what you guys are talking about, I guess I can call apro in to do this.