Flue adjustment ?
Joe.G
Member Posts: 213
Hi, I was wondering, on my new flue pipe there is a weight adjustment, I was wondering how should this be adjusted? Should hte flue be open the hole time the boiler is running? or only at start up, any info would be great thanks.
0
Comments
-
It should only be adjusted with
a draft gauge or manometer by a professional!0 -
Is there a way to get it close?0 -
.
there are many things that you can screw up by playing with the draft regulator---its not a toy if you don't have instruments leave it alone//// if its noisy or you get a small amount of soot from it you may have a problem---changing the adjustments will not fix whatever problem you might be having it will more than likely cause more problems--0 -
I had a boiler installed, i then replaced all of the piping going out to my chimney inculding the flue The flue door stays open the whole time the boile ris running, i was just wondering where I want it to be, what can happen if it is not adjusted right.0 -
> I had a boiler installed, i then replaced all of
> the piping going out to my chimney inculding the
> flue The flue door stays open the whole time the
> boile ris running, i was just wondering where I
> want it to be, what can happen if it is not
> adjusted right.
0 -
you want it to be maintaining a minimum draft --of ----whatever the manufacturer of the boiler/burner package recommends --you need to know what the overfire draft is supposed to be ----problems can include burning up the diffuser,blast tube,overheating the nozzle can cause sooting ,plugging the boiler destroying the fiber combustion chamber -------------you need to know what you're overfire draft is supposed to be --the chimney draft should be at 1 in water column higher than that and the regulator maintains you overfire draft through the seasons0 -
Isn't a typical chimney draft...
about -.06", and a typical over-fire draft -.02" on oil boilers? Of course it varies, but where do you see 1"?0 -
.
that would be a "difference" of .01 w.c. and overfire depends on the burner boiler combo--- mine is recommended minimum of .03 overfire0 -
-.06?
In the flue????
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Just trying to confirm...
some typical readings you guys see in the field. Is it that unusual to see -.02" over the fire, -.04" in the flue (before the draft regulator), and -.06" in the stack (after the draft regulator, essentially the chimney reading). Am I not remembering things correctly?0 -
Ahhhhh
.06 AFTER the draft regulator. Thought you meant before.
We typically see -.02 to -.03 before.
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
That's why I prefer...
to confine the designation "flue" to the areas before the regulator (or hood), and the designation "stack" to the areas after the regulator (or hood). I know I'm pretty much alone on that thought (here, at least) - but how many times do you hear the flue draft reading being given as the chimney draft reading - they are not the same!0 -
I have no idea what you guys are talking about, I guess I can call apro in to do this.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements