2 pipe steam w/ dry returns?
Jamie_6
Jamie_6 Member Posts: 710
We are working on a two pipe steam system which has dry returns and it looks as if someone has made random changes to its integrity. The steam mains are hung along the basement ceiling with the returns below them approximately 10". Someone has installed a F & T trap at the end of the steam main and connected to the return. Should this have been done this way? I have also noticed that the only venting on the entire system is at the radiators.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
  • Fred Harwood
    Fred Harwood Member Posts: 261
    Two-pipe steam
    Sounds OK, since the F&T also vents air (ensure that it does, don't take it for granted). Once the main is filled with steam, the the rads vent next.
    Are you sure that the rads have no condensate returns? If not, you essentially have a one-pipe system with an elevated wet return protected by the F&T, if you know what I mean.
    Steamhead Member Posts: 18,211
    Jamie, is this Vapor
    or 2-pipe air-vent? If it's Vapor, that F&T does the same job as those crossover thermostatic traps on Dunham, Hoffman, Webster and other Vapor systems. The radiator vents may have been added by a non-heating man.
    If it's 2-pipe air-vent, that F&T is unusual but it could work OK. However I'd switch to a standard main vent setup.