Zone Valve vs Zoned Circulator Comparison Check List
RB_2
Member Posts: 272
Seems to be a reoccurring topic so here is a checklist for making comparisons...
I think its also necessary that when making comparisons its important to look at applications, arrangement of equipment, comfort expectations, types of loads and all available products.
Operating cost
will vary somewhat with zoned pumps. Depends on how much energy you are moving while consuming X amount of electrical energy.
Siggy use a wire to water formula
E= .00302 X density of fluid X flow gpm x operating head
divided by wattage draw of circ.
So an 80 watt pump moving 10 gpm at 6 feet of heat would be 13.7% efficient.
E= .00302 X 60.7 X 10 X 6 divided by 80 watts
Use this same pump to move a mere 2 gpm @2 ft in a typical small radiant zone and look at the efficiency!
This is my biggest gripe about zoning with circ pumps. And without balance valves the circs could be running way off of the curve.
You would need to know these numbers for every pumped flow to be accurate in the comparison chart, wouldn't you?
hot rod
A Thanks Giving Treat
Hi Hot Rod,
I have just sent you a Thanks Giving Treat on the subject...and yes your comments are all valid...
Gobble Gobble
rb0 -
Now that's a serious treat
nothing like a full on ASHRAE response. Thanks
Now I'm really fowled up!
hot rod
- 167 Indoor-Air Quality