Buderus G115

RoosterBoy
Member Posts: 459
hi on the g115 model 28 the d.o.e Heating capacity is 98,000 btu.
my load is about 53,000. but next year I want to add indirect water heater and in 2 years a small addition on the house. if I have my contractor remove the baffle plates and put a smaller nozzle on the burner. will that bring me to around 78,000 btu.
and next year when I add my hot water heater I can have them put back in to bring it back up to 98,000 I just don't want to short cycle the burner this year.
thanks
my load is about 53,000. but next year I want to add indirect water heater and in 2 years a small addition on the house. if I have my contractor remove the baffle plates and put a smaller nozzle on the burner. will that bring me to around 78,000 btu.
and next year when I add my hot water heater I can have them put back in to bring it back up to 98,000 I just don't want to short cycle the burner this year.
thanks
0
Comments
-
don't do it...
it is not that "oversized". Messing around with the baffles and down firing are not a good plan w/ the 115. kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
hi kevin so even with this year my load is 53,000 without indirect 85,000 ibr will not short cycle my burner?
thanks0 -
Dont underfire the burner.
We are already underfired a little. Adding a indirect doesnt change your demand. We drive the indirect with enough btu@ the right gpm that the heat isnt off for that long.0
This discussion has been closed.
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 971 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements