Buderus G115

RoosterBoy
Member Posts: 459
hi on the g115 model 28 the d.o.e Heating capacity is 98,000 btu.
my load is about 53,000. but next year I want to add indirect water heater and in 2 years a small addition on the house. if I have my contractor remove the baffle plates and put a smaller nozzle on the burner. will that bring me to around 78,000 btu.
and next year when I add my hot water heater I can have them put back in to bring it back up to 98,000 I just don't want to short cycle the burner this year.
thanks
my load is about 53,000. but next year I want to add indirect water heater and in 2 years a small addition on the house. if I have my contractor remove the baffle plates and put a smaller nozzle on the burner. will that bring me to around 78,000 btu.
and next year when I add my hot water heater I can have them put back in to bring it back up to 98,000 I just don't want to short cycle the burner this year.
thanks
0
Comments
-
don't do it...
it is not that "oversized". Messing around with the baffles and down firing are not a good plan w/ the 115. kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
hi kevin so even with this year my load is 53,000 without indirect 85,000 ibr will not short cycle my burner?
thanks0 -
Dont underfire the burner.
We are already underfired a little. Adding a indirect doesnt change your demand. We drive the indirect with enough [email protected] the right gpm that the heat isnt off for that long.0
This discussion has been closed.
Categories
- 120.8K All Categories
- 83.8K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 416 Carbon Monoxide Awareness
- 36 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 116 Geothermal
- 154 Indoor-Air Quality
- 2.9K Oil Heating
- 49 Pipe Deterioration
- 753 Plumbing
- 5.3K Radiant Heating
- 358 Solar
- 13.9K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 37 Industry Classes
- 70 Job Opportunities
- 14 Recall Announcements