CV RATING
Rob_15
Rob_15 Member Posts: 8
I have a question reguardng cv ratings.I do not quite understand how to size items properly (mixing valve etc).
If someone can explain it I would greatly appreciate it.
  • Tim Doran_2
    Tim Doran_2 Member Posts: 131
    Finding the pressure drop
    When the Cv is known and the desired flow is known the pressure drop in ft/hd is found by (flow/Cv)^2*2.31
    Tim D.
  • From a
    previous thread:
    DATE: Apr 23, 2001
    SUBJECT: Post from the past
    NAME: Alan R. Mercurio
    Hi, this was asked before and answered by I believe Dave Wood. I hope he
    does not mind my sharing his knowledge?
    CV Is:
    defined as the gpm of water that can pass through a valve with a one psi
    drop in pressure.Cv = Q/square root of the dp is the formula you can use,
    where Q is the number of gallons per minute and dp is the pressure drop,
    orQ = Cv x (SqRt of dp).With a valve with a Cv of 6.3, you get 6.3 gpm
    with a one pound differential or 2.31 feet of head.If your pressure drop is
    increased 2 psi or 4.62 feet, the gpm through the valve is about 8.9
    gpm.Hope it helps. DWood
    http://www.oiltechtalk.com
    The attached CV table is from Robert Bean. Thanks, Robert.
  • Tim Doran_2
    Cv Calculator
    Here is a quick calculator.
    Tim D.