Looking for examples of Flue Gas Condensation
Gerard Hazel
Member Posts: 1
I am developing a seminar for presentation at ISH in October on the causes and effects of Flue Gas Condensation
in Boilers and Breeching/Chimney Systems. If you have a story or a picture or a burner tube and would like to share your experience please contact me via E-Mail.
Thanks,
Gerry Hazel
Thanks,
Gerry Hazel
Here are some examples
Mis applied copper tube boilers, without return water temperature protection. Often with micro zoned short cycling, to boot
hot rod
Chimney pics
Here are few pics of a plugged chimney.
Flue gas condensation rotted the clay liner and the liner collapsed.
All of the combustion products were venting into the basement and rising into the living space.
Mark H
flue condensation
bacharach has some on there site0 -
boiler corrosion
Those pics look like they are pool heaters, am I correct? Teledyne and Raypak always tried to rely on their thermal bypass in the header to control condensation in the heat x.0 -
Condensation
I see often where a masonry chimney deteriorates due to condensation. The terra-cotta liner flakes and cracks, the chimney block gets efflorecsense and the morter between blocks gets like mush.Stucco loosens and falls off. Paint peels. Stains appear on the outside surface. I am going to reline a chimney with said problems in a few weeks. I,ll send pictures.0 -
This is a pool boiler.
Should have shrunk it but it looks better close up.0 -
flue condensation
Are you including water heaters(low water temperatures) in this presentation and that flue liners don't necessarily solve the problem?(Baracharch pictures) I will also be at ISH0
- 120 Geothermal