3 Phase Motors
Servicewiz_2
Member Posts: 28
I am very interested in any information that can be obtained on the resistance reading (OHMS) on three Phase A/C motor windings.Any help is greatly appreciated!!!
Servicewiz
Servicewiz
Resistance
It kind of hard to say an exact number. Typically low .5 to 2 ohms phase to phase. And you BETTER read infinite from phase to ground or extremely high if your using a megger.0 -
> Servicewiz
The readings L1-L2, L1-L3, L2-L3 should all be the same and above zero...also check the three legs to ground.
Not really sure what you are looking for or why.
Vic Plank
Lancaster PA0 -
> can _BR_ > be obtained on the resistance
> reading (OHMS) on _BR_ > three Phase A/C
> motor windings.Any help is _BR_ > greatly
> appreciated!!! _BR_ > Servicewiz
> _BR_ _BR_
> check the three legs to ground. Not really sure
> Vic
> Plank Lancaster PA
why do you want to know the ohms--test it static then test after operating and windings have expanded ----if you are trying to diagnos a motor going off on overload -there are a few more things to look at --contacts in line starter,wires going to it ,control panel ,wire connections,motor load ,phase inbalance----use the middle contact for the low leg --correct voltage within 10% of rating -etc...0