I have 3 zones, two copper fin baseboard and one converted gravity radiator. When ever either of the baseboard zones call I get passive flow through the radiator zone. Brute circulators with internal flow checks are installed on the return line on a 1.25" manifold. What did I do wrong? Would heavier cast flow checks be more effective? Any suggestions would be helpfull.
Thank you, Art Goedeke.
  • ARTIEGEE
    GRUNFOS IFC
  • hr
    hr Member Posts: 6,106
    In some cases
    you need check protection on both the supply and return lines. Waem water will migrate up either pipe, regardless of direction arrows :) Especially when the piping rises vertically from the boiler.
    It could also be in your piping layout. Is this a primary secondary piping arrangment?
    Got pictures or drawings?
    hot rod