three piece pumps
bovide
bovide Member Posts: 13
When you encounter a leaking 3 piece circulator, do you change the gasket or always change the bearing assembly?
  • gerry gill
    gerry gill Member Posts: 3,083
    we
    change the whole bearing asembly.
    gwgillplumbingandheating.com
    Steamhead Member Posts: 18,217
    I try to check
    to see if the circulator was sized properly. If it is, I replace the bearing. If not, I recommend a new, properly-sized circulator.
    If the HO has not been oiling the bearings like they should, I recommend using a wet-rotor unit that does not need oiling- if one is available in the size the system needs.
    Consulting
  • Whenever a circulator
    needs more than a coupling & motor rings, & a comparable wet rotor, or permanently lubricated pump is available (& appropriate), we make the change.
    The advantages are obvious to our customers. Low wattage motors, 3-5 years w/o repairs, no lubricating oil dripping on their floor, or on my burner or boiler jacket. And. No couplings to go bang-bang-bang @ 1 AM. It is also a good time to install iso flanges on those jobs w/o valves.