Do Spirovents need to be cleaned?
Ex Maine Doug
Member Posts: 161
I have a bit of air still circulating around that I thought would be collected by the Spirovent. Do these things need to be cleaned once a system is put into service? It is plumbed as per the Wall and hissed when first filled and when the next zone was added so it was working.
Thank-you.
Thank-you.
Slabs Leak
Anywhere within your heating that the pipe go under a slab ?0 -
Shut off the water.....
Shut the domestic off and monitor the gauge. Is the pressure droping?? Those vents remove air very well. If it continues, look for your leak... BOC0 -
sometimes
the little vent hole will become plugged and not allow the air to vent. A paper clip generally will dislodge the bugger
Watch your system pressure, if it drops to zero you may have a leak causing the noise you hear.
hot rod
i think they do,
i always put a drain valve at the end of a straight tube underneath it, that the exp tank and feed - tee into - so that i can flush it down
- the same bail of screens that make the air pop out of the mix, will make dirt drop out too
but dont expect to get too much dirt out of a reg spirovent - cause - there just isnt enough space at the bottom of it to hold a lot - that's why they make a special units,
called spirotrap and a combo unit, - these are a must for a gravity conversion job that generates a lot of dirt due to the cast iron
http://www.spirotherm.com/dirt/ http://www.spirotherm.com/combination/
