lwco problem
ed wallace
Member Posts: 1,612
just installed a no.67 lwco millivolt system and a 24 volt auto water feed lwco works properly as to shutting system down when low on water but when boiler is on the autowater feed keeps cycling im kind of stumped any one have any ideas ???
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=256&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
isolation
Do you have the 24v and the millivolt properly isolated ???? How are the controls wired ??? I assume the water feed is a small timer type and not a float.0 -
Dirty Water
Maybe you introduced some oil to the boiler water during the install.If so the water will surge triggering the switch in the #67 for more water. You can check to see if the water needs cleaning by ;Shutting off the "lower" pet cock on the gauge glass assembly . Run the boiler until it produces steam, then open the gg assemblies drain . If the condensate comes over the top then the boiler needs to be skimmed. Skimming will remove the floating oil slick .....0 -
lwco problem
the milivolt wires are on the 2 and 3 terminals top 2 terminals the 24 volt water feed is wired to 3 and 4 bottom 2 terminals i think maybe a bad switch or float any other ideas ??? i dont think its an oil issue water is clean and not bouncing around
- 167 Indoor-Air Quality