hydronic water quality
ScottMP
ScottMP Member Posts: 5,882
Of this circulator.
This is about six years old, Peerless gas fired, power vented, with four zone valves.
Customer said the circulator was making a whining noise. This is what we found. If you look close you can see the shiney spots where the impellor was hitting the build up, of what I assume is a iron sludge.
Scott
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=237&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
  • hr
    hr Member Posts: 6,106
    This is why
    I hammer so much about water quality and treatment.
    What type of distribution system? Piping material? Operating temperatures? Fill system on, or off?
    Check for leaks, sure looks like a problem caused by continous make up water. But if the system ran without a good purger, the O2 could cause this much damage even without additional fresh water.
    Clean em and treat em, or be prepared for a lot more of this. Especially on lower temperature systems.
    Fairly typical fill water ay 60°F has an O2 of 10ppm. At 140°F 4.72. At 180°F look for 2.7.
    A good inhibitor needs O2 scavangers, ph buffers, azoles for copper and brass protection, a plating chemical, and a dispersant for scale and sludge control.
    A good cleaner before final fill will get rid of oils and flux residue and remove any food source for bacteria to get a hold of.
    I have a shelf full of components that look like that. Some after only two years service!
    hot rod
  • hr
    The boiler
    wonder what it looks like inside? Efficiency? Good thing you didn't mention the serial number :)
    Sure like to see the boiler mans recommend some adequate cleaning methods and product choices. What %s of the residential boilers out there are looking like this, do you suppose.
    Give them a new boiler and split that old one open! We'd all like to see that innards.
    Tick, tick, tick :(
    hot rod
  • ScottMP
    HR
    This is a copper finned baseboard system with no reset. Three zones of heat and one indirect, so this unit does not have a long down period. That means this build up happened with a running circulator. I know I was shocked to see it.
    Not only could you here the pump screaming but I could feel poor circulaton when I first got the call. My thoughts also went to the cast iron block and its condition.
    How sad.
    Scott
  • hr
    Like I always say
    it didn't ship from the factory looking like that :)
    If you haven't found something wrong, something ain't right.
    hot rod