Recplacing Steam Heat
Options
Sunnie
Member Posts: 1
Have steam heat and would like to vacation for 3 months. Have no one available to fill boiler every 2-3 days. Whats my best solution?????????
0
Comments
-
You are filling the boiler
every 2 to 3 days ? I would bet there is a leak somewhere - the vents , a return pipe , something .
On a new install where the homeowners vacation for a long time , or they are elderly and cannot get down in the basement , I recommend using 2 probe LWCOs . No need to flush the standard control , like a 67 , but they do need to be checked every year for buildup on the probes . You can connect an auto feeder to the LWCO also , but being gone for 3 months at a clip , I wouldn't want to know the damage the feeder could cause if something happens and it fills the boiler continuously ( very rare though ) .
Vacation for 3 months ? I envy you .0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 76 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements