look at this near boiler piping
Fred P
Member Posts: 77
this boiler doesnt look piped right. I may be wrong, but is the equalizer supposed to be below the side tapping (is there even an equalizer on here??) and is the hartford loop a little on the small side??
I noticed there is drain tapping off the return pipe, thats a good idea.
This is a 1 pipe system in my neighbors house.. just wondering what you guys think of the way it was piped out.
It was piped from only 1 tapping and goes straight up into a 90 elbow...
isn't it amazing...
forrest gump would say, ugly is as ugly does...0 -
i guess that means
you dont like the way this looks.. but is it acceptable?? would it meet "code" so to speak...
I dont like the way it looks either, but Im not in the business... but Im learning!0 -
not even close, Jim
Show me a header with an equalizer at the end that is 24" above the water line.
Noel0 -
Let me try
That tee isn't looking too good- where it comes out of the boiler should 90 UP, get to at least 24" above the water line, then 90 into a horizontal "header", then after you pipe into the main, you'll have a 90 facing down, which connects to the return. This is called the equalizer.
Gary
what about the hartford loop?
It looks like there is a small one there, is it acceptable or did they cut corners here too??0 -
the size would be in the
installation instructions which can usually be found online at the boilers manufacturers web site..0 -
so whats happening here? the steam is coming out
the side of the boiler, what happens next? Does the water content immediatly drop down and back into the return?
is this piping setup causing a lot of wet steam to go up into the main and rads??
Im trying to picture this in my head0 -
It all depends on the steam velocity.
If the pipe is big enough and the boiler output low enough you may see alot of the water drop out.
Boilerpro0 -
funny thing
is that this thing works, although the homeowner complains of having to add water every few days in winter season.. Although her efficiency isnt so great, we get about the same gas bills and my boiler is 55 years old and takes over an hour to get steam into the rads...hers takes about 20 mins0 -
If it takes an hour
to get steam into your radiators, the boiler may be the cause- and it may not be. Are your steam mains insulated, and are there vents at the ends- if so, what make & model? How long are the mains and what pipe size?
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Consulting0 -
my boiler is being replaced
next week and a main vent will be added since there isnt one there now or ever before. And I insulated the mains a couple of years ago..didnt do much except keep the basement cooler and more bearable..0 -
its a bryant and the website does not
have the instruction manual online0 -
I think it's water
Is that green thing a pump??
The picture does noy show enough information.0 -
steam & water
a split system0 -
its a taco circulating pump
for hot water baseboard.. Is an aquastat required for hot water off boiler?0 -
Aquastat
No the boiler should be warm enough.The aquastat would only add parts and make it more diffacult to work on later.
The KISS method works best on these.0 -
Actually, it's good to have one
on a split system like this. If only the hot-water zone is calling for heat (not the steam zone) you don't want to get the boiler hot enough to make steam. So the aquastat would cut the burner off at 180 degrees or so. If the steam zone (or both zones) calls for heat, the aquastat is bypassed and the boiler can make steam.
Consulting0 -
by-pass
It should also have a bypass from the return water of baseboard so you can temper the water going to the baseboard system when the boiler is making steam.
Ant
A better picture would really help, the controls and that pump
would lead me to believe that somethings wrong. I think that your neighbor needs a bigger basement, that boiler is a real tight pack.0
- 167 Indoor-Air Quality