old vapor system
joe_14
joe_14 Member Posts: 138
i have been working on an old vapor system,it has a barnes &jones #1 condensator with a b&j vent trap#2. i think the condensater is not working properly so i replaced the presuretrol with a vaporstat set it at 8oz cuts in at 4oz. i also replaced the two b&j angle traps used to vent the mains. raditors are heating now. the problem iam having is that i am seeing a small amount of vapor coming out of the &2 VENT TRAP. is this normal or do i have some raditor traps leaking by. is the &2 vent trap still available or can i replace with a main vent. thank you for your help
joe.g
    Steamhead Member Posts: 18,431
    You probably have some leaking traps
    Find them and fix them. If the vent trap is shot and B&J no longer makes it, a large main vent like a Gorton #2 will work.
    The Return Trap (Condensator) can be rebuilt- try Tunstall if B&J no longer makes parts.
    Consulting
  • joe_14
    condensator
    b&j said they had a new one in stock 3000.00 dollars customer dosent want to spend that money. using the vaporstat i hope will get him thru the winter. i the spring i will take apart condensator clean and rebuild i will call tunstall do you have there number and address.thanks for the help steamhead,i value your opinion and have great respect for your knowledge.
    thank you joe.g.
  • Joe,
    I have the paperwork for the B&J condensator at work (I hope I can find it). I can fax it to you Monday, if you like.
    http://www.tunstall-inc.com/
    Noel
  • noel, can you post it here,
    i'd like to see it too.-thanks
  • If I get near a scanner I can.
    I have to find it first.
    Noel