Venting gas boilers
Jack_23
Jack_23 Member Posts: 153
Regardless of requirements, performance will be much better with a lined chimney. Analyze the cost of the new boilers plus the relining system BEFORE selection of the equipment. You may want to go with Catagory III system rather than a Cat I. III's can be side wall vented with a special vent system (which may vary by manuf). I's can be vertically (nat'l draft)vented or side wall vented with the addition of a power venter. BTW, a masonry chimney is 11th century technology venting a 21st century appliance. Does not work well.
  • bob_17
    bob_17 Member Posts: 14
    venting gas boilers
    I am really confused about venting gas boilers into a clay lined, indoor chimney..The manufacturer's instructions seem to be evasive At best.. Where are the regulations for Ma.The only thing I am able to find is authored by chimney liner manufacturers..Can any one help?
  • Harvey_5
    Harvey_5 Member Posts: 7
    Do your boilers have combustion air? I have seen the old
    clay lined chimneys form condensation. Back in my residential days, we used to install a chimney liner.
  • ed wallace
    ed wallace Member Posts: 1,612
    ma regulations
    In Ma.on gas installs you must line the chiney and also have makeup air usally utilazing a fan iun the can system
  • paul lessard_2
    paul lessard_2 Member Posts: 192
    read this
    someone needs to sign off on the condition
  • paul lessard_2
    not always
    category 1 can be vented with b vent,chimney,listed liner system or "special vent" ...the chimney needs to be signed off by someone before replacement equipment goes in...or so i hear..I guess It depends on what the local inspector thinks or knows..:=) paul