HOT AIR HEAT CONTROLS
My neighbor has an older house with an equally old hot air heating system. I think the manufacturer is Lumitrol. On the unit itself is a control box for the burner and blower, possibly a temp. range adjustment. It seems to be giving the unit some trouble running correctly. I haven't found any info about this company. How can they get a replacement controller?
  • Dana
    Dana Member Posts: 126
    Honeywell will probably have a replacement. You'll need to know the correct model # of the controller or exactly what it does. It's probably the fan limit control.
  • Berne Ferry
    Berne Ferry Member Posts: 3
    Thanks. It's a dual control, one for heat and the other for the fan. Can I check the Honeywell website for something like this?
  • Robert O'Connor_4
    Robert O'Connor_4 Member Posts: 88
    L4064
    is a fan a limit control by Honeywell.Probably is similar to what you need.
    Check out specifications at:
    http://hbctechlit.honeywell.com.
    regards,
    Robert
  • HP80
    HP80 Member Posts: 55
    You will most likely need to remove the control to measure the length of insertion before anyone can help you. Unfortunately the manufacturers of these controls gave each OEM a different part number and somewhere down the line we realize that we need cross referencing to these but it was too late. Please be careful when replacing this unit as it may have delay timing built into it and if the incorrect timing is selected you could be putting these people in a potentially dangerous situation.
  • Berne Ferry
    Thanks. I'll look into it.