auto water feeder
stan_2
stan_2 Member Posts: 12
If it's recommended to install a water meter with an automatic water feeder on a steam boiler, what kind of gpm's and in what period of time should I be looking for that would indicate trouble?
  • On Residential systems
    you should be able to account for almost ALL water that registers on the meter. All you should see is what replaces blowdowns of the boiler and controls.
    Any water beyond that is the beginnings of a leak. Look for the cause. If you don't find it, watch for the water to increase.
    Like anything else that you monitor, the first reading doesn't mean much. Readings over a period of time establish a baseline. Variations from THAT are what you are looking for. There might be a seasonal variation, reflecting run time, which is acceptable, but investigate strange water usage.
    Noel
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,687
    Look into
    the Hydrolevel feeder. It has a built-in electronic water meter. Mighty fine idea!
    Retired and loving it.
  • Dale
    Dale Member Posts: 1,317
    Check out
    Dan, went to the link and found a real cool tee in their installation instructions, an FOEM tee with room for the probe, that really looks professional.
  • DanHolohan
    That's been around for a while and I like it.
    These guys make really nice stuff
  • Al Letellier
    Al Letellier Member Posts: 781
    hydrolevel
    Right on, Dan. I've been using the Hydolevel autofeeder and it's a great unit. Solved several flooding problems with it last heating season, When steam systems got a real workout. The meter make life so easy........