lennox wiring
airhead
Member Posts: 9
can anyone help me with lennox low volt wiring for heat pump? lennox stat model # 36G7101.Terminals R M V W Y. thank you.
It has been a very long time but,
I'll give it a try. Why not upgrade the stat to something in english and not Lennoxesse?
I hope:
R = R
W = W
Y = Y
V = reversing valve
M = Motor or blower motor
Put a 3 amp ATO or ATC automotive type fuse in the hot or red side of the low voltage coming off the transformer and then run through the above to see if I am right. Do the same at the air handler and the outdoor unit.
What I can not remmeber is if the Lennox guys ste the heat pump reversing valve to fail in heat or cool mode.
Good luck
Mark
Lennox wiring
Airhead,
R=Reversing Valve=O
M=Compressor Contactor=Y
V=24v power=R
Y=2nd stage heat=W2
F=Blower relay=G
A=Ambient sensor=T
L=Service Light=L
3=24v common=C
Hope that helps!0