lennox wiring
airhead
airhead Member Posts: 9
can anyone help me with lennox low volt wiring for heat pump? lennox stat model # 36G7101.Terminals R M V W Y. thank you.
  • Mark A. Custis
    Mark A. Custis Member Posts: 247
    It has been a very long time but,
    I'll give it a try. Why not upgrade the stat to something in english and not Lennoxesse?
    I hope:
    R = R
    W = W
    Y = Y
    V = reversing valve
    M = Motor or blower motor
    Put a 3 amp ATO or ATC automotive type fuse in the hot or red side of the low voltage coming off the transformer and then run through the above to see if I am right. Do the same at the air handler and the outdoor unit.
    What I can not remmeber is if the Lennox guys ste the heat pump reversing valve to fail in heat or cool mode.
    Good luck
    Mark
  • Jared M
    Jared M Member Posts: 31
    Lennox wiring
    Airhead,
    R=Reversing Valve=O
    M=Compressor Contactor=Y
    V=24v power=R
    Y=2nd stage heat=W2
    F=Blower relay=G
    A=Ambient sensor=T
    L=Service Light=L
    3=24v common=C
    Hope that helps!