buderus question
Options
wjh
Member Posts: 8
I am replacing my existing boiler and water heater with a buderus g115/28 and indirect water heater.I like what i have read about the buderus logamatic control hs2109.I have been told to forget that control and use a priority relay with cold start or if I wanted to keep the boiler warm use a triple aquastat set at a low temp.Should if keep the boiler warm or go cold start? What has been your experience with the logamtic control hs2109?--Any help or suggestions would be very helpful--thank you
0
Comments
-
HS-2109
The HS-2109 allows you better control of the tank temp and prioritizes the DHW.
You may want to consider the HS-2107 which offers outdoor reset.
Cold start is no problem for the Buderus. With an indirect fired water heater I would not recommend maintaining a low temp in the boiler as it gains you nothing.
Hope this helps!
Mark H
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
I agree with Mark
Cold start is not a problem with the 115. I would highly recommend the 2107 control with outdoor reset. This alone will save you some $$$ on your heating bill. The 2107 is also programmable for setback temps. There are a bunch of factory installed programs in it right out of the box or you can customize it any way you want. Think long and hard about the extra $300-$400 expense now vs. 10-20% savings on your fuel bill for as long as you own that boiler. Energy prices will never go down.0 -
Right On!!
Steve's got it pegged...selecting the right control is critical and the integral Logomatic control with outdoor reset would be a no-brainer. This boiler is designed for cold start.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
With Buderus
There is no point to maintaining a "low temp" as the circulator supplying the domestic hot water heat exchanger will not start untill the boiler temp is 10 *F above the temp in the tank.
Chuck Shaw0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements