Dan-Foss KVS ?
Greg Wallace
Member Posts: 3
Here's just one more simple example of why people have nothing but great things to say about this guy. He's the genuine article. Let me know if you ever get back to Wisconsin. Maybe we could have lunch with Dennis "the driver" Wood.
Greg
Greg
Danfoss KVS -5 Sensor?
Hello, I found this Danfoss valve the other day @ a cust. house..Danfoss says they have no such valve! It calls itself a T stat and has a remote sensor non electric in a well @ the end of a 3/4 " manifold.3 zone valves ,1 tempering loop w/a flo check..Radiant system,,I am no artist!!!Is there another valve by sone1 else?or should I pipe in a 3way valve???Something doesn't look right to me but fairly new to radiant!Age of system??5 to 10Y/O ? I had the body PN nad still no help on their site either..Thanks for your time Richard0 -
Fast service!!
Thanks Dan I'll check the site out..Love trying to figure out other peoples ideas..Richard0 -
Danfoss Kvs-5
Chances are the valve is a 2 way VMT series with a RAVV self contained actuator. It is often used as a injection valve...as per your application but with a correct installation.
The Kv is the Euro equivalent to Cv.
The PN is the pressure rating in bars. 1 bar = 14.7 psi.
Contact Danfoss Calgary for schematics, Dave Heath, Todd Skuce or Brian Wheeldon at 403-236-9569.
rb
I say
Bring Back The Bean!!!Retired and loving it.0 -
Thankyou all
for your help!!They say you get a new wrinkle in your brain for everything you learn,well more wrinkles on the brain and face after this one ...Will be calling Danfoss Monday...Richard0 -
I'll take you up on that offer...
Lunch with you and D would be grand!
rb0 -
Valve with KV5
Robert's right (again), you've got a 2-way injection style application with a VMT series (part #065B8961) valve. If you need the RAVV control, there are a few different temperature ranges available, check the dial for the range shown in Celsius. Thanks again Robert!
Bill0 -
Thankyou again
for all the info.! " Celsius "you say!!!!!.Now I have to learn that.!!!!Bummer.LOL The wall is a !!!LIFE saver
Hopeto return the favor....Rich0